The Nail Salon
will be bit delayed until I get on the roof. And by the way, if there is equipment on the roof that requires servicing, you need a permanent ladder. If you understood English it would help because my Cambodian is a little rusty. You would at least know why I left without going on the roof.
""20% Off" is in regards to the ladder."
Yup, about that...........that would have been a genuine LOL moment for me.
I feel your pain - be there a time or two.
A serious question though: as I recall, the 2009 IMC requires a permenant ladder when the roof surface is greater than 16' above grade (correct me if wrong here - going from memory.) If you are inspecting a changout on an existing structure, and the ladder was not required under the code when the structure was built, do you require the installation of a permenant ladder to service the new equipment?
Darren Emery said:
I feel your pain - be there a time or two. A serious question though: as I recall, the 2009 IMC requires a permenant ladder when the roof surface is greater than 16' above grade (correct me if wrong here - going from memory.) If you are inspecting a changout on an existing structure, and the ladder was not required under the code when the structure was built, do you require the installation of a permenant ladder to service the new equipment?
I am going by memory too and I think the height distinction has to do with whether the ladder will be inside or outside the building and it's 15'. New equipment requires a ladder.
2009 IMC reads the same as 2003 IMC
2003 IMC 306.5 Equipment and appliances on roofs or elevated structures.
Where equipment and appliances requiring access are
installed on roofs or elevated structures at a height exceeding
16 feet (4877 mm), such access shall be provided by a permanent
approved means of access, the extent of which shall be
from grade or floor level to the equipment and appliances’ level
service space. Such access shall not require climbing over obstructions
greater than 30 inches (762 mm) high or walking on
roofs having a slope greater than 4 units vertical in 12 units horizontal
(33-percent slope).
Permanent ladders installed to provide the required access
shall comply with the following minimum design criteria:
1. The side railing shall extend above the parapet or roof edge
not less than 30 inches (762 mm).
2. Ladders shall have rung spacing not to exceed 14 inches
(356 mm) on center.
3. Ladders shall have a toe spacing not less than 6 inches (152
mm) deep.
4. There shall be a minimum of 18 inches ( 457 mm) between
rails.
5. Rungs shall have a minimum 0.75-inch (19 mm) diameter
and be capable of withstanding a 300-pound (136.1 kg)
load.
6. Ladders over 30 feet (9144mm)in height shall be provided
with offset sections and landings capable of withstanding
100 pounds (488.2 kg/m2) per square foot.
7. Ladders shall be protected against corrosion by approved
means.
Catwalks installed to provide the required access shall be
not less than 24 inches (610mm)wide and shall have railings as
required for service platforms.
Exception: This section shall not apply to Group R-3 occupancies.
We must have an amendment because if the roof is 15' or more above the floor, the means of access shall be from inside the building with no exceptions for under 16'.
I am at home with only a 2007 Ca. mechanical code and I just noticed that it only applies to gas utilization equipment and does not mention "requiring service". I will have to look at the 2011 tomorrow.
The big one we run it to with nail salons is the HVAC requirments, the 20 CFM per person to the outside throws them for a loop everytime, and most of the time they try and open with out it by saying they didn't understand it or other places do have to do that why do we? Man I love my job...............sometimes
Justin