The NFPA's Take on Type Construction - Using the NFPA 70 as an example

jar546

CBO
Joined
Oct 16, 2009
Messages
12,816
Location
Not where I really want to be
As we slowly try to mirror certain sections of the NFPA and ICC Codes, we still some differences. Here is an example of how the electrical community determines type construction and below is from the IBC. What are some differences that may cause problems in interpretation?

NFPA 70
Type I is a fire-resistive construction type. All structural elements and most interior elements are required to be noncombustible. Interior, nonbearing partitions are permitted to be 1- or 2-hour rated. For nearly all occupancy types, Type I construction can be of unlimited height.

Type II construction has three categories: fire-resistive, one-hour rated, and nonrated. The number of stories permitted for multifamily dwellings varies from two for nonrated and four for one-hour rated to 12 for fire-resistive construction.

Type III construction has two categories: one-hour rated and nonrated. Both categories require the structural framework and exterior walls to be of noncombustible material. One-hour rated construction requires all interior partitions to be one-hour rated. Nonrated construction allows nonbearing interior partitions to be of nonrated construction. The maximum permitted number of stories for multifamily dwellings and other structures is two for nonrated and four for one-hour rated.

Type IV construction includes traditional heavy timber construction and mass timber construction. In heavy timber construction, the structural framework and the exterior walls are required to be noncombustible except that wood members of certain minimum sizes are allowed. In mass timber construction, structural elements of cross-laminated timber (CLT) are permitted. Allowable building height for mass timber is much higher than for heavy timber.

Type V construction has two categories: one-hour rated and nonrated. One-hour rated construction requires a minimum of one-hour rated construction throughout the building. Nonrated construction allows nonrated interior partitions with certain restrictions. The maximum permitted number of stories for multifamily dwellings and other structures is two for nonrated and three for one-hour rated.

Here is the IBC (minus tables)

602.2Types I and II.​

Types I and II construction are those types of construction in which the building elements listed in Table 601 are of noncombustible materials, except as permitted in Section 603 and elsewhere in this code.

602.3Type III.​

Type III construction is that type of construction in which the exterior walls are of noncombustible materials and the interior building elements are of any material permitted by this code. Fire-retardant-treated wood framing complying with Section 2303.2 shall be permitted within exterior wall assemblies of a 2-hour rating or less.

602.4Type IV.​

Type IV construction is that type of construction in which the exterior walls are of noncombustible materials and the interior building elements are of solid wood, laminated wood, heavy timber (HT) or structural composite lumber (SCL) without concealed spaces. The minimum dimensions for permitted materials including solid timber, glued-laminated timber, structural composite lumber (SCL) and cross-laminated timber and details of Type IV construction shall comply with the provisions of this section and Section 2304.11. Exterior walls complying with Section 602.4.1 or 602.4.2 shall be permitted. Interior walls and partitions not less than 1-hour fire-resistance rating or heavy timber complying with Section 2304.11.2.2 shall be permitted.

602.5Type V.​

Type V construction is that type of construction in which the structural elements, exterior walls and interior walls are of any materials permitted by this code.
 