Forget for a minute that there may be other reasons for a wider stair, we're considering only code requirements for this thought exercise. CBC in my case. Think of a generic office building with multiple levels, including high-rises, but not anything tall enough to trigger a third stair per CBC 403.5.2
For a building with two interior exit stairs the largest occupant load than can be served is 500 per floor (CBC Table 1006.3.2). Let's also install a voice alarm per 907.5.2.2 in our imaginary building. And we're sprinkled.
500 occupants x .2" capacity factor = 100"
100"/2(stairs) = 50" per stair
1011.2 requires a minimum stair width of 44" - Got that.
1009.3.2 requires 48" between handrails but only if not sprinkled so it doesn't apply.
So I don't see anything that would require me to provide a stair (x2) wider than 50" in a 20 story office building with 50,000 SF floor plates (just to give a specific example). Am I missing anything? Is there anything in the code that would push these stairs wider than 50"?
For a building with two interior exit stairs the largest occupant load than can be served is 500 per floor (CBC Table 1006.3.2). Let's also install a voice alarm per 907.5.2.2 in our imaginary building. And we're sprinkled.
500 occupants x .2" capacity factor = 100"
100"/2(stairs) = 50" per stair
1011.2 requires a minimum stair width of 44" - Got that.
1009.3.2 requires 48" between handrails but only if not sprinkled so it doesn't apply.
So I don't see anything that would require me to provide a stair (x2) wider than 50" in a 20 story office building with 50,000 SF floor plates (just to give a specific example). Am I missing anything? Is there anything in the code that would push these stairs wider than 50"?