• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Thermal Barrier

docgj

Silver Member
Joined
Oct 29, 2009
Messages
123
Location
PA
2006 IRC. I can't locate a requirement for insulation (kraft faced fiberglass) to be covered on walls. I know I must be overlooking it somewhere. Could someone quote me Chapter and Verse?

docgj
 
I think this is what you are looking for.

It's not a thermal barrier that's required for the kraft facings,

Thats for foam, section 314

SECTION R316

INSULATION

R316.1 Insulation. Insulation materials, including facings,

such as vapor retarders or vapor permeable membranes

installed within floor-ceiling assemblies, roof-ceiling assemblies,

wall assemblies, crawl spaces and attics shall have a

flame-spread index not to exceed 25 with an accompanying

smoke-developed index not to exceed 450 when tested in

accordance with ASTM E 84.

Exceptions:

1. When such materials are installed in concealed

spaces, the flame-spread and smoke-developed limitations

do not apply to the facings, provided that the

facing is installed in substantial contact with the unexposed

surface of the ceiling, floor or wall finish.

2. Cellulose loose-fill insulation, which is not spray

applied, complying with the requirements of Section

R316.3, shall only be required to meet the smoke developed

index of not more than 450.
 
That will work. I must have overlooked that 3 to 4 times!

Thanks!