Thermal Barrier

Fritz

Bronze Member
Joined
Feb 12, 2010
Messages
59
Location
Fargo, ND
We have been asked to accept 3/4" plywood as be equivlent to 1/2 sheetrock for a thermal barrier.

On face value, section 721, it would appear to be so. But I cannot come across any tested documentation.

I know some roofing assemblies use it as a separation, but that I believe is in a tested assembly.

Any thoughts or directions to go look for some information.
 
I haven't found it in the section yet,

Seems like the tables as you mentioned are assemblys only.
 
Last edited by a moderator:
$ $ $ $



Fritz,



Since you have been asked to approve the 3/4" plywood as a substitute,

..ask that documentation be provided to you that will allow the

substitution.....( i.e. - where are "they" obtaining their approval from ? )

Isn't the burden of approval on the person asking ? :o



$ $ $ $
 

"The performances

of the 5/8-inch hardboard composite, the

3/4-inch mixed species plywood, the 5/8-inch particleboard,

and the 3/4-inch southern pine plywood were

comparable to the performance of the 1/2-inch regular

gypsum board."

Where does it say if that was tested with thte foam backer as accotrding to the same article,




"The presence of insulation behind the

panel reduced the times to achieve a 250°/325° F rise

in temperature."

Also, this looks like 1982, , , not that it maybe matters . . .



 
Wasn't really arguing one way or another. My gut reaction was that it would probably protect in a similar fashion, Googled it, and came up with the report. Not my issue, just adding information.
 
A 15/32" Wood sheathing is equal to 1/2" Gypsum Wall Board when you are seeking a 15-Min. Thermal Barrier
 