FYI:
A TIA has been issued to NFPA 25 Inspection, Testing and maintenance of Water -Based Fire Protection Systems
(See April NFPA News)
*******************************************************************
Reference: 3.6.4.1.1 Premixed Antifreeze Solution (New), 5.3.4, and A.5.3.4
TIA 11-1 (SC 11-3-6/TIA Log #1014)
Pursuant to Section 5 of the NFPA Regulations Governing Committee Projects, the National Fire Protection Association has issued the following Tentative Interim Amendment to NFPA 25, Standard for the Inspection, Testing, and Maintenance of Water-Based Fire Protection Systems, 2011 edition. The TIA was processed by the Technical Committee on Inspection, Testing, and Maintenance of Water-Based Systems, and was issued by the Standards Council on March 1, 2011, with an effective date of March 21, 2011.
A Tentative Interim Amendment is tentative because it has not been processed through the entire standards-making procedures. It is interim because it is effective only between editions of the standard. A TIA automatically becomes a proposal of the proponent for the next edition of the standard; as such, it then is subject to all of the procedures of the standards-making process.
1. Add a new definition as 3.6.4.1.1 to read as follows:
3.6.4.1.1 Premixed Antifreeze Solution. A mixture of an antifreeze material with water that is prepared by the manufacturer at a factory with a quality control procedure in place that ensures that the antifreeze solution remains homogeneous.
2. Revise 5.3.4 to read as follows:
5.3.4* Antifreeze Systems. Annually, before the onset of freezing weather, the antifreeze solution shall be tested using the following procedure:
(1) Using installation records, maintenance records, information from the owner, chemical tests, or other reliable sources of information, the type of antifreeze in the system shall be determined.
a) If the type of antifreeze is found to be a type that is no longer permitted, the system shall be drained completely and replaced with an acceptable solution.
b) If the type of antifreeze cannot be reliably determined, then the system shall be drained completely and replaced with an acceptable solution.
(2) If the antifreeze is not replaced in accordance with step 1, test samples shall be taken at the top of each system and at the bottom of each system.
a) If the most remote portion of the system is not near the top or the bottom of the system, an additional sample shall be taken at the most remote portion.
b) If the connection to the water supply piping is not near the top or the bottom of the system, an additional sample shall be taken at the connection to the water supply.
(3) The specific gravity of each solution shall be checked using a hydrometer with a suitable scale or a refractometer having a scale calibrated for the antifreeze solution.
(4) If any of the samples exhibits a concentration in excess of what is permitted by NFPA 25, the system shall be emptied and refilled with a new acceptable solution. If a concentration greater than what is currently permitted by NFPA 25 was necessary to keep the fluid from freezing, alternate methods of preventing the pipe from freezing shall be employed.
(5) If any of the samples exhibits a concentration lower than what is necessary to keep the fluid from freezing, the system shall be emptied and refilled with a new acceptable solution.
5.3.4.1 The use of antifreeze solutions shall be in conformity with state and local health regulations.
5.3.4.1.1* Listed CPVC sprinkler pipe and fittings shall be protected from freezing with glycerin only. The use of diethylene, ethylene, or propylene glycols shall be specifically prohibited.
5.3.4.2* Antifreeze solutions shall comply with one of the following:
(1) The concentration of a glycerin solution measured in an existing system shall be limited to 50% by volume.
(2) Newly introduced solutions shall be factory premixed antifreeze solutions of glycerin (chemically pure or United States Pharmacopoeia 96.5%) at a maximum concentration of 48% by volume.
(3) The concentration of a propylene glycol solution measured in an existing system shall be limited to 40% by volume.
(4) Newly introduced solutions shall be factory premixed antifreeze solutions of propylene glycol (chemically pure or United States Pharmacopoeia 96.5%) at a maximum concentration of 38% by volume.
(5) Other solutions listed specifically for use in fire protection systems.
5.3.4.3 The antifreeze solution shall be tested at its most remote portion and where it interfaces with the wet pipe system.
5.3.4.4 Where antifreeze systems have a capacity larger than 150 gal (568 L), tests at one additional point for every 100 gal (379 L) shall be made.
5.3.4.4.1 If the results indicate an incorrect freeze point at any point in the system, the system shall be drained and refilled with new premixed antifreeze.
5.3.4.4.2 For premixed solutions, the manufacturer’s instructions shall be permitted to be used with regard to the number of test points and refill procedure.
4. Remove Table 5.3.4.1(a) and 5.3.4.1(b) and add Table 5.3.4.1 as follows:
(Tables and Guide didn’t copy well)
(See NFPA News in April)
A TIA has been issued to NFPA 25 Inspection, Testing and maintenance of Water -Based Fire Protection Systems
(See April NFPA News)
*******************************************************************
Reference: 3.6.4.1.1 Premixed Antifreeze Solution (New), 5.3.4, and A.5.3.4
TIA 11-1 (SC 11-3-6/TIA Log #1014)
Pursuant to Section 5 of the NFPA Regulations Governing Committee Projects, the National Fire Protection Association has issued the following Tentative Interim Amendment to NFPA 25, Standard for the Inspection, Testing, and Maintenance of Water-Based Fire Protection Systems, 2011 edition. The TIA was processed by the Technical Committee on Inspection, Testing, and Maintenance of Water-Based Systems, and was issued by the Standards Council on March 1, 2011, with an effective date of March 21, 2011.
A Tentative Interim Amendment is tentative because it has not been processed through the entire standards-making procedures. It is interim because it is effective only between editions of the standard. A TIA automatically becomes a proposal of the proponent for the next edition of the standard; as such, it then is subject to all of the procedures of the standards-making process.
1. Add a new definition as 3.6.4.1.1 to read as follows:
3.6.4.1.1 Premixed Antifreeze Solution. A mixture of an antifreeze material with water that is prepared by the manufacturer at a factory with a quality control procedure in place that ensures that the antifreeze solution remains homogeneous.
2. Revise 5.3.4 to read as follows:
5.3.4* Antifreeze Systems. Annually, before the onset of freezing weather, the antifreeze solution shall be tested using the following procedure:
(1) Using installation records, maintenance records, information from the owner, chemical tests, or other reliable sources of information, the type of antifreeze in the system shall be determined.
a) If the type of antifreeze is found to be a type that is no longer permitted, the system shall be drained completely and replaced with an acceptable solution.
b) If the type of antifreeze cannot be reliably determined, then the system shall be drained completely and replaced with an acceptable solution.
(2) If the antifreeze is not replaced in accordance with step 1, test samples shall be taken at the top of each system and at the bottom of each system.
a) If the most remote portion of the system is not near the top or the bottom of the system, an additional sample shall be taken at the most remote portion.
b) If the connection to the water supply piping is not near the top or the bottom of the system, an additional sample shall be taken at the connection to the water supply.
(3) The specific gravity of each solution shall be checked using a hydrometer with a suitable scale or a refractometer having a scale calibrated for the antifreeze solution.
(4) If any of the samples exhibits a concentration in excess of what is permitted by NFPA 25, the system shall be emptied and refilled with a new acceptable solution. If a concentration greater than what is currently permitted by NFPA 25 was necessary to keep the fluid from freezing, alternate methods of preventing the pipe from freezing shall be employed.
(5) If any of the samples exhibits a concentration lower than what is necessary to keep the fluid from freezing, the system shall be emptied and refilled with a new acceptable solution.
5.3.4.1 The use of antifreeze solutions shall be in conformity with state and local health regulations.
5.3.4.1.1* Listed CPVC sprinkler pipe and fittings shall be protected from freezing with glycerin only. The use of diethylene, ethylene, or propylene glycols shall be specifically prohibited.
5.3.4.2* Antifreeze solutions shall comply with one of the following:
(1) The concentration of a glycerin solution measured in an existing system shall be limited to 50% by volume.
(2) Newly introduced solutions shall be factory premixed antifreeze solutions of glycerin (chemically pure or United States Pharmacopoeia 96.5%) at a maximum concentration of 48% by volume.
(3) The concentration of a propylene glycol solution measured in an existing system shall be limited to 40% by volume.
(4) Newly introduced solutions shall be factory premixed antifreeze solutions of propylene glycol (chemically pure or United States Pharmacopoeia 96.5%) at a maximum concentration of 38% by volume.
(5) Other solutions listed specifically for use in fire protection systems.
5.3.4.3 The antifreeze solution shall be tested at its most remote portion and where it interfaces with the wet pipe system.
5.3.4.4 Where antifreeze systems have a capacity larger than 150 gal (568 L), tests at one additional point for every 100 gal (379 L) shall be made.
5.3.4.4.1 If the results indicate an incorrect freeze point at any point in the system, the system shall be drained and refilled with new premixed antifreeze.
5.3.4.4.2 For premixed solutions, the manufacturer’s instructions shall be permitted to be used with regard to the number of test points and refill procedure.
4. Remove Table 5.3.4.1(a) and 5.3.4.1(b) and add Table 5.3.4.1 as follows:
(Tables and Guide didn’t copy well)
(See NFPA News in April)