Toilet Room Corridor Door in I-1 with Rescue Hardware

100eyeballs

Bronze Member
Joined
Sep 7, 2011
Messages
45
Location
Michigan
Typically in I-2 hospitals a toilet room located in a corridor is allowed (required) to have emergency rescue hardware and there is no problem since corridor construction is non-rated smoke partitions, with non-rated doors.

Trying to apply the same application in a I-1 facility, with 1-hour fire rated fire partition corridor requirement and 20 minute fire-rated opening protective doors. Rescue hardware is not allowed on fire-rated doors from what I understand. Is there a way to allow these doors by code?
 
100eyeballs said:
Typically in I-2 hospitals a toilet room located in a corridor is allowed (required) to have emergency rescue hardware and there is no problem since corridor construction is non-rated smoke partitions, with non-rated doors.Trying to apply the same application in a I-1 facility, with 1-hour fire rated fire partition corridor requirement and 20 minute fire-rated opening protective doors. Rescue hardware is not allowed on fire-rated doors from what I understand. Is there a way to allow these doors by code?
The problem isn't so much the hardware, but the frame. Because the door has to swing in both directions, a cased opening frame must be used. This type of frame has no stops, and nothing to limit the spread of smoke/flames around the door edges. It won't pass a fire test. Can you swing the doors out of the bathroom instead? Then you won't need rescue hardware.
 
Can you swing the doors out of the bathroom instead? Then you won't need rescue hardware.
Depending upon the "required" width of the I-1 corridor, the outswinging door might swing

too much in to the "required" corridor width (RE: 2006 Edition of the IBC, Section 1005.2).

.
 