DSinspector
REGISTERED
I was hoping someone could give me a bit of guidance with this one. The townhome in question is using Georgia Pacific Shaftliner for 2hr rated assembly. In the manual it requires 3/4" clearance from combustible materials. Under special circumstances item 7 states that the 3/4" clearance can be omitted if the metal framework of the party wall is covered by one of a variety of materials. This is immediately followed by "attic areas not accessible do not require the 6" wide gypsum strips" This seems to contradict the whole omittance clause or suggest that combustion cannot happen in a non-accessible attic. Can someone shed some light on this for me? The full exception is below:
7. The required 3/4” (19 mm) air space can be eliminated if the metal framing is covered on both faces with 6” (152 mm)
wide, 1/2” (12.7 mm) DensArmor Plus® Fireguard C® or 1/2” (12.7 mm) ToughRock® Fireguard C® or 5/8” (15.9 mm)
ToughRock® Fireguard X® or 5/8” (15.9 mm) DensArmor Plus® Fireguard® gypsum board strips. The gypsum board strips
are attached with 1” (25.4 mm) drywall screws spaced 12” (305 mm) o.c. to the metal framing. This primarily occurs in
accessible attic areas. Attic areas not accessible do not require the 6” (152 mm) wide gypsum board strips.
7. The required 3/4” (19 mm) air space can be eliminated if the metal framing is covered on both faces with 6” (152 mm)
wide, 1/2” (12.7 mm) DensArmor Plus® Fireguard C® or 1/2” (12.7 mm) ToughRock® Fireguard C® or 5/8” (15.9 mm)
ToughRock® Fireguard X® or 5/8” (15.9 mm) DensArmor Plus® Fireguard® gypsum board strips. The gypsum board strips
are attached with 1” (25.4 mm) drywall screws spaced 12” (305 mm) o.c. to the metal framing. This primarily occurs in
accessible attic areas. Attic areas not accessible do not require the 6” (152 mm) wide gypsum board strips.