Hello all,
Is there any reason that plumbing piping is not allowed in the common wall between duplex residences? My plumbing engineer is saying that we can't and I cannot find a code reason why.
I am working on a renovation project with various apartments built in the early 80s. There are various plans including duplexes and townhomes. Some were not separated properly (1-hr instead of 2, no attic separation, etc.). One townhouse was designed properly with a 2-HR wall and a parapet, but it has plumbing running through it, including washer boxes, dryer vents, water piping, and waste vents.
I've been searching the forums and the code and I found where the code prohibits this in the townhouses. Specifically, IRC2006 Section R317.2: "A common 2-hour fire-resistance-rated wall is permitted for townhouses if such walls do not contain plumbing or mechanical equipment, ducts or vents in the cavity of the common wall."
First, this section doesn't prohibit piping in general. Only those 4 specific things. Is water piping allowed?
Second, I cannot find where (or if) it prohibits plumbing in a duplex separation. That would be a 1-HR wall between two-family dwellings per R317.1. I then read R317.3.2 for membrane penetrations which leads to R317.3.1.1 "Penetrations shall be installed as tested in the approved fireresistance-rated assembly."
The way I read it, we should be able to run vent piping within the cavity of the 1-HR rated wall, then back out of the wall and up thru the roof. There are through penetration UL listings for this application where you essentially just fire seal it and call it a day. Am I missing something?
Thanks in advance.
-LP
Is there any reason that plumbing piping is not allowed in the common wall between duplex residences? My plumbing engineer is saying that we can't and I cannot find a code reason why.
I am working on a renovation project with various apartments built in the early 80s. There are various plans including duplexes and townhomes. Some were not separated properly (1-hr instead of 2, no attic separation, etc.). One townhouse was designed properly with a 2-HR wall and a parapet, but it has plumbing running through it, including washer boxes, dryer vents, water piping, and waste vents.
I've been searching the forums and the code and I found where the code prohibits this in the townhouses. Specifically, IRC2006 Section R317.2: "A common 2-hour fire-resistance-rated wall is permitted for townhouses if such walls do not contain plumbing or mechanical equipment, ducts or vents in the cavity of the common wall."
First, this section doesn't prohibit piping in general. Only those 4 specific things. Is water piping allowed?
Second, I cannot find where (or if) it prohibits plumbing in a duplex separation. That would be a 1-HR wall between two-family dwellings per R317.1. I then read R317.3.2 for membrane penetrations which leads to R317.3.1.1 "Penetrations shall be installed as tested in the approved fireresistance-rated assembly."
The way I read it, we should be able to run vent piping within the cavity of the 1-HR rated wall, then back out of the wall and up thru the roof. There are through penetration UL listings for this application where you essentially just fire seal it and call it a day. Am I missing something?
Thanks in advance.