• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Ttransfer switch in a exterior stairwell enclosure

knightj

Member
Joined
Jul 21, 2011
Messages
22
Location
Winchester VA
2 story, Type 3B office building, non sprinkled. Cliant wants to locate the transfer switch to a new generator install in one the exterior exit enclosures of his building. Would this cross the line of using this stairway for any pourpose than as an exit. What say you.
 
is this going to be inside the exit enclosure, or mounted on the outside of the building, on an exterior wall, enclsong the exit stair. if its outside, probably ok, if its inside the stairs, no go
 
IMHO - It would be crossing the line..... because the penetrations into the stairway do not directly serve the stair way.

707.8 Penetrations. Penetrations in a shaft enclosure shall be

protected in accordance with Section 712 as required for fire

barriers.

707.8.1 Prohibited penetrations. Penetrations other than

those necessary for the purpose of the shaft shall not be permitted

in shaft enclosures.
 
Unless it is part of a legally required emergency system(emergency lighting).......But I would probably say no......

Builder Bob said:
IMHO - It would be crossing the line..... because the penetrations into the stairway do not directly serve the stair way.707.8 Penetrations. Penetrations in a shaft enclosure shall be

protected in accordance with Section 712 as required for fire

barriers.

707.8.1 Prohibited penetrations. Penetrations other than

those necessary for the purpose of the shaft shall not be permitted

in shaft enclosures.
 
Builder Bob said:
IMHO - It would be crossing the line..... because the penetrations into the stairway do not directly serve the stair way.707.8 Penetrations. Penetrations in a shaft enclosure shall be

protected in accordance with Section 712 as required for fire

barriers.

707.8.1 Prohibited penetrations. Penetrations other than

those necessary for the purpose of the shaft shall not be permitted

in shaft enclosures.
This is the right answer!
 
Agree

Architect1281 said:
This guy says NO 1022.1 Enclosures required ..........(at the end) "An exit enclosure shall not be used for any purpose other than means of egress."
Architect1281 nailed it. Not no but hell no.
 
purpose

There might be light and a switch that might work better with electricity.

Why make a big deal out of it?
 