I have a remodel project that has two exit stairways, Stair A discharges directly to the exterior, and Stair B discharges through an exit discharge lobby (1028.1 exception 1). The entrances to both exit stairways at all floors are sufficiently separated (1/3 building diagonal, sprinklered). However, the exit door of Stair A and the lobby exit door discharge to the same general area and are only 18' apart, which is where the question lies. I did the original design in-house (I'm not an architect, no architect required for this project) but we recently hired an architect to help speed the project along, and they are saying that these doors that lead to the exterior need to be separated by the 1/3 distance. I disagree with this, as 1007.1.1 seems to only apply to the doors leading from the exit access. I don't find anything that limits the remoteness of these doors. RLGA's comment seems to agree with my opinion, but I wanted to present my specific situation. This project is under IBC 2018, in North Dakota.