Tim Mailloux
Hypothetically, say you have a two story building with an atrium or any similar two story volume that is atmospherically open to the 2nd floor. Even though there is no physical floor at the upper volume of the atrium (a giant hole in the floor), does the area of the atrium get added to the 2nd floors gross floor area?
Based on the definition of Floor Area, Gross and the corresponding code commentary I would say it does.
[BE] FLOOR AREA, GROSS. The floor area within the inside perimeter of the exterior walls of the building under consideration, exclusive of vent shafts and courts, without deduction for corridors, stairways, ramps, closets, the thick-ness of interior walls, columns or other features. The floor area of a building, or portion thereof, not provided with surrounding exterior walls shall be the usable area under the horizontal projection of the roof or floor above. The gross floor area shall not include shafts with no openings or interior court.
Commentary
Gross floor area is that area measured within the perimeter formed by the inside surface of the exterior walls. The area of all occupiable and non occupiable spaces, including mechanical and elevator shafts, toilet rooms, closets and mechanical equipment rooms, are included in the gross floor area. This area could also include any covered porches, carports or other exterior space intended to be used as part of the building’s occupiable space. Both gross and net floor areas are used for the determination of occupant load in accordance with Table 1004.5
The fact that the only exclusions from the gross floor area are vent shafts (aka natural ventilation shaft with no roof) and interior courts (also with no roof), and that stairways, mechanical shafts and elevator shafts (large floor openings) are specifically included in the gross floor area would lead me to believe that a large atrium floor opening would also be included in the gross floor area of the upper floor. An interpretation I received years ago from an AHJ was that if the space in question has a floor or roof overhead, it gets included in the gross floor area whether it has a floor or not.
Commentary