• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Two Ways A Transformer Can Be Grounded & Bonded

Those are two ways to ground the secondary side of a transformer as a Separately Derived System (SDS).

When the primary side system is grounded, another option for grounding the secondary side as a non-SDS is by connecting the primary side grounded conductor to one of the secondary conductors. Then no Grounding Electrode Conductor is required, there is no System Bonding Jumper, and the Supply Side Bonding Jumper is just called an EGC.

Just FYI.

Cheers, Wayne
 
Those are two ways to ground the secondary side of a transformer as a Separately Derived System (SDS).

When the primary side system is grounded, another option for grounding the secondary side as a non-SDS is by connecting the primary side grounded conductor to one of the secondary conductors. Then no Grounding Electrode Conductor is required, there is no System Bonding Jumper, and the Supply Side Bonding Jumper is just called an EGC.

Just FYI.

Cheers, Wayne
I agree. Which method do you see used?
 
The only difference is the location of the SBJ and where the GEC terminates. Why is it better to have those at the transformer?

Cheers, Wayne
Two reason:
1) It is the most common so you have consistency with inspections (not a big deal)
2) The facility can treat all panelboards as sub-feeds, since the neutral and EGC are separated. Sometimes you can't see the transformer or know that a panelboard is fed by a transformer, so it again, creates consistency. Option two may seem confusing to maintenance staff that does not know better.
3) I prefer it. I'll pass whatever method a contractor uses as long as it is compliant, regardless of my personal preferences.
 