mtlogcabin
SAWHORSE
We have some inconsistency in shutting down Type I Hood ventilation system upon activation of the suppression system. Some jurisdictions shut down the entire system others just the make up air and leave the exhaust on regardless of the type of extinguishing sytem. Our jurisdiction has been under the IFC since 2002 while every one else in the state remained under the UFC. They are now adopting the 2009 IFC.
This was all I could find
2006 IFC 904.11.3.1 Ventilation system.
Commercial-type cooking equipment protected by an automatic carbon dioxide extinguishing system shall be arranged to shut off the ventilation system upon activation.
Our own FD required the supply to be shut down and the exhuast to remain running but I can not find a code section to back this up
This was all I could find
2006 IFC 904.11.3.1 Ventilation system.
Commercial-type cooking equipment protected by an automatic carbon dioxide extinguishing system shall be arranged to shut off the ventilation system upon activation.
Our own FD required the supply to be shut down and the exhuast to remain running but I can not find a code section to back this up