Type III-B? Metal Building w/ Wood Framed Mezzanine
Sector3
Portland, OR
This is an existing building. We are looking at a prefabricated steel framed building, insulated, metal siding, business use. At some point, a mezzanine was added consisting of wood structural columns and LVLs, and engineered wood I-joists framing the floor.
Does the mezzanine kick us from Type II-B into Type III-B?
Thank you for your input.
In accordance with Table 601 III-B has 2-hr. load bearing exterior walls.
II-B should be non-combustible provided with the exceptions of section 603.
V-B would fit construction type.
  • Like
Reactions: JBI
Thanks for your input. The building has no bearing walls, it's a steel frame. So all walls are non-bearing.
Then it could III-B
See 704.10 in reference to footnote f, if the metal or steel that supports the exterior wall is framed as part of the interior wall will need to be protected.
Each methods of assembly will need to be considered on a case by case basis to determine the appropriate construction type.
@Francis Vineyard , @steveray ,
Thanks for writing back. The steel frame is 'interior' of the exterior wall, as the exterior wall passes continuously on the outside of the structure. However, I do not believe the exterior walls are 2 hour.
So it sounds like we'll need to dig into V-B and see how that affects the building as a whole.
  • Like
Reactions: JBI
Back in the day didn't we call these "Butler" built buildings? Even allowed them to be installed on property lines in industrial areas.
  • Like
Reactions: JBI