A co-worker just reminded me IBC 2308 is not applicable because our ground snow exceeds 50 psf
2308.2 Limitations.
Buildings are permitted to be constructed in accordance with the provisions of conventional light-frame construction, subject to the following limitations, and to further limitations of Sections 2308.11 and 2308.12.
1. Buildings shall be limited to a maximum of three stories above grade plane. For the purposes of this section, for buildings assigned to Seismic Design Category D or E, cripple stud walls shall be considered to be a story.
Exception: Solid blocked cripple walls not exceeding 14 inches (356 mm) in height need not be considered a story.
2. Maximum floor-to-floor height shall not exceed 11 feet, 7 inches (3531 mm). Bearing wall height shall not exceed a stud height of 10 feet (3048 mm).
3. Loads as determined in Chapter 16 shall not exceed the following:
3.1. Average dead loads shall not exceed 15 psf (718 N/m2) for combined roof and ceiling, exterior walls, floors and partitions.
Exceptions:
1. Subject to the limitations of Sections 2308.11.2 and 2308.12.2, stone or masonry veneer up to the lesser of 5 inches (127 mm) thick or 50 psf (2395 N/m2) and installed in accordance with Chapter 14 is permitted to a height of 30 feet (9144 mm) above a noncombustible foundation, with an additional 8 feet (2438 mm) permitted for gable ends.
2. Concrete or masonry fireplaces, heaters and chimneys shall be permitted in accordance with the provisions of this code.
3.2. Live loads shall not exceed 40 psf (1916 N/m2) for floors.
3.3. Ground snow loads shall not exceed 50 psf (2395 N/m2).
4. Vasd as determined in accordance with Section 1609.3.1 shall not exceed 100 miles per hour (mph) (44 m/s) (3-second gust).
Exception: Vasd as determined in accordance with Section 1609.3.1 shall not exceed 110 mph (48.4 m/s) (3-second gust) for buildings in Exposure Category B that are not located in a hurricane-prone region.
5. Roof trusses and rafters shall not span more than 40 feet (12 192 mm) between points of vertical support.
6. The use of the provisions for conventional light-frame construction in this section shall not be permitted for Risk Category IV buildings assigned to Seismic Design Category B, C, D, E or F.
7. Conventional light-frame construction is limited in irregular structures assigned to Seismic Design Category D or E, as specified in Section 2308.12.6.