To answer CDA, the GA assembly is the submitted design. However, since they have failed to provide the 1" gap, they are now asking to use the UL design, which is a little different. So now I need to review it as a revised design.
To Ron, I totally understand your logic, and if it were that easy I would be a happy man. BUT, a general explanatory note to the GA design allows larger studs, which they have used. In some cases a double 3 5/8", in others a 6" and a 3 5/8". So the bracing could work with the walls closer together. UL also permits larger studs. So the drawing of U420 shows a gap but I can't find a minimum gap size, whereas the GA, USG and at least one other drawing of U420 show a minimum of 1". What's a girl to do? Maybe UL will get back to me...............if not, in the absence of a minimum I don't think I have a basis to not approve it.
If the minimum gap is to limit temperature transfer from the back of the gypsum panels to each other I think they have improved the condition because their distance is greater than the minimum. If it is to limit transfer across the studs from one wall to the other I think they have made it worse. AND, I don't even know if that is the reason for the gaps in the first place. This is where I have to rely on the published assemblies, they just don't quite match up and since I have one document that is more restrictive, and the other document somewhat ambiguous, I am leaning on the more restrictive. However, since the GA is based on U420 I am right back befuddled.