• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Ultra-Dog Security Bars in Occupied Buildings

Gordon

Member
Joined
Apr 26, 2010
Messages
20
Location
Kansas
Has anyone accepted the use of Ultra-Dogs while a building is occupied?

Of course, they are intended for the "after hours environment" but I'm curious to know if anyone has accepted them in "unusual" security situations.

Personally, I don't think it is defensible & there should always be another technical solution that does not impair the means of egress, but always looking out for other possible approaches.

Thanks
 
Don't see how this complies with the code for several reasons:

1.) special knowledge or effort ---- never seen 'em before so how do they work 1008.1.8 Door operations. Except as specifically permitted

by this section egress doors shall be readily openable from the egress side without the use of a key or special knowledge

or effort.

2.) If the panic bars or other latching action is used, this is a second action to open the door.

1008.1.8.5 Unlatching. The unlatching of any door or leaf shall not require more than one operation.

Funny that this section of hte code doesn't specify if occupied or not ----
 