NEC Section 250.8 outlines the only acceptable methods for connecting equipment grounding conductors, grounding electrode conductors, and bonding jumpers. These connections are critical to ensuring the electrical system has a reliable and low-impedance path back to the source in the event of a fault.

The code lists eight permitted methods:
  1. Listed pressure connectors
  2. Terminal bars
  3. Pressure connectors listed as grounding and bonding equipment
  4. Exothermic welding
  5. Machine screw-type fasteners that engage at least two full threads or are secured with a nut
  6. Thread-forming machine screws that engage at least two full threads in the enclosure
  7. Connections that are part of a listed assembly
  8. Other connections specifically permitted in the NEC

A common point of confusion is the use of listed pressure connectors. Twist-on wire connectors, even if not green in color, may be used for grounding and bonding as long as they are listed. The color is not a code requirement, although green is often used for identification.

Machine screws and thread-forming machine screws are specifically identified as acceptable. This language intentionally excludes other screw types, such as sheet metal screws and drywall screws, which are not acceptable for grounding and bonding connections. Coarse-threaded screws do not meet product certification standards because they cannot reliably engage the two full threads required in a metal box or enclosure.

The takeaway is simple: use only the methods listed in 250.8 and avoid improvisation. The wrong connector or fastener can compromise the grounding path, creating a safety hazard and a clear code violation.
ChatGPT Image Aug 9, 2025, 11_48_20 AM.png
 
1. Listed pressure connectors
As luck would have it, I have pictures.

They come in sizes for a reason.

DSCN1544.JPG

The number and size wire is predetermined by the manufacturer. It is never more than two.

IMG_4489.JPG


A proprietary tool is required to close the crimp. Pliers are not allowed.

IMG_3400.JPG

The last picture shows the indent marks that are found if the correct tool was used to close the crimp however there is still an issue with the size.

IMG_5310.JPG
 
Last edited:
They thought it through almost to the end.

IMG_5517.JPG

This guy was not going to give up.

IMG_2213 - Version 2.JPG

An inch short might as well be a mile.

IMG_3508.JPG

Here's that lack of respect showing up again. That they would leave this for me to find says volumes about their work.

IMG_5371.jpg

Okay, that's enough on C-Taps. Should we do ground rods next?
 