Understanding NEC 445.18: Generator Disconnecting Means and Emergency Shutdown Requirements
Generators play a critical role in backup and emergency power systems, but they also pose electrical and mechanical hazards if not properly controlled. NEC 445.18 establishes essential safety measures for disconnecting and shutting down generators to protect personnel, emergency responders, and property. Let’s break down each section of this code to understand how it applies to real-world generator installations.(A) Disconnecting Means
What it says:- Generators (except cord-and-plug-connected portable ones) must have a disconnecting means that can simultaneously open all ungrounded conductors (hot wires).
- The disconnecting means must be lockable in the open position as per NEC 110.25 to prevent accidental or unauthorized re-energization.
If you have a permanently installed standby generator, it must have a way to completely disconnect it from the system. This is typically done with a manual or automatic transfer switch (ATS) with a built-in disconnect or a separate circuit breaker designed for isolation. Lockability ensures that workers can safely service the generator without risk of it starting unexpectedly.
(B) Emergency Shutdown of Prime Mover
What it says:- The generator must have a way to shut down the prime mover (the engine that drives the generator).
- This shutdown mechanism must:
- Disable all prime mover start control circuits, ensuring the generator cannot restart automatically.
- Require a mechanical reset before it can restart.
This requirement ensures that once the generator is shut down, it cannot restart without manual intervention. This is important for preventing dangerous situations where a generator might restart unexpectedly due to an automatic control system. Many generators have manual reset buttons that must be pressed before the unit can be restarted after a shutdown.
Can the emergency shutdown also serve as the disconnecting means?
Yes, if the shutdown mechanism is lockable in the open position. This means that in some cases, a single device can serve both as the emergency shutdown and the generator disconnect—reducing the need for additional equipment.
(C) Remote Emergency Shutdown (New for 2020 NEC)
What it says:- Generators larger than 15 kW must have a remote emergency stop switch that meets the same shutdown requirements as 445.18(B).
- The remote switch must be located outside the generator enclosure or equipment room.
For safety, generators over 15 kW (such as many residential standby generators and commercial backup units) must have a shutdown switch away from the generator itself. This allows someone to stop the engine from a safe location in case of an emergency, such as overheating, fuel leaks, or other failures.
Example: If a 22 kW standby generator is installed on one side of a house, and the ATS (automatic transfer switch) is on the other side, a remote shutdown switch should be located in an easily accessible spot outside the home—often near the ATS or main electrical panel.
(D) Emergency Shutdown for One- and Two-Family Dwellings (New for 2020 NEC)
What it says:- For non-portable generators, an emergency shutdown device must be installed outside the dwelling in a readily accessible location.
This aligns with other emergency power disconnection requirements in the NEC (such as NEC 230.85 for service disconnects). The goal is to ensure that firefighters or emergency personnel can quickly shut down power in a residential setting without needing to enter the home or approach the generator directly.
Best Practice: If multiple emergency disconnects are required (for example, solar power, battery storage, and a generator), they should be grouped together in a logical location. While not explicitly required by code, this makes it easier for first responders to quickly shut off power.
(E) Generators Installed in Parallel
What it says:- When multiple generators operate in parallel, their disconnecting means must isolate the output terminals from the paralleling equipment.
- The disconnecting means does not have to be at the generator itself.
Large facilities such as hospitals, data centers, and industrial plants often run multiple generators in parallel for increased reliability. In these cases, electrically operated breakers control the connection between generators and the main power system.
Key Consideration:
A standard emergency shutdown switch does not meet the requirement for an isolation disconnect in parallel generator setups. Instead, specialized paralleling switchgear with interlocking breakers is used to prevent dangerous backfeeding.
Why These Rules Matter
NEC 445.18 ensures that generators can be safely disconnected and shut down in an emergency. Without these safeguards, workers could be exposed to unexpected re-energization, emergency responders might struggle to shut off power during a fire, and automated systems could restart a generator in unsafe conditions.
- Every stationary generator needs a disconnecting means that can be locked open.
- Emergency shutdown switches must disable the engine and prevent automatic restart.
- Generators over 15 kW require a remote emergency stop outside the enclosure.
- Residential standby generators must have an exterior emergency shutdown switch.
- Parallel generator systems require special isolation methods.