I have a Garden Style Apartment project in NC that has an unenclosed breezeway with a single stair. At one end of the breezeway we have storage closets. We have operated on the principal that this is an unenclosed egress stair (open on one side that leads to a public way).The breezeway(more accurately the "landing") and unenclosed exterior stair is separated from the rest of the building (units) via a 1 hour construction (when connecting less than 4 stories) with fire-rated wall assembly UL-U311, and with 45 minute rated doors, and (for the storage closets) by 10’ of distance and 45 minute rated doors.Further we are protecting the buildings with a NFPA 13R sprinkler system.The code official saying that our "stair" is open to the "corridor" and not to a "public way".He says we must provide a stair enclosure and get rid of the storage closets.We must have storage closets in order to meet a federal program that requires exterior storage closets for each unit.It appears that even enclosed stairs need to exit on a public way so how does one do this?It is no excuse but we have built literally dozens of these buildings in other jurisdictions in NC over the course of 20 years with no problem.Is it back to the drawing board or is there any way that this configuration will work.See attached planView attachment 2593