LGreene
REGISTERED
Many moons ago I was taught that if there is a fire door that is no longer in use as a door, the door had to be removed and the opening filled with construction equivalent to the wall rating. The point was that the rating of an opening protective is typically lower than the rating of the wall construction, so when you close a fire door and push a storage cabinet up against it, the door may not provide enough protection against the increased fuel load. The 2010 edition of NFPA 80 (referenced by the 2012 IBC) says:
5.1.2 Removal of Door or Window. Where a door or window opening is no longer in use, the opening shall be filled with construction equivalent to that of the wall.
I posted something on my blog about this (http://idighardware.com/2014/05/ww-hidden-door/), and someone commented that I was wrong...that the door didn't have to be removed, it could be replaced with another door equal to the wall rating, or somehow "treated" to provide the same protection as the wall. I don't think this is commonly done, and once the storage cabinet is against the door, the door may not be able to be opened for the annual fire door inspection to verify the rating or that it is code-compliant.
My question for you is...if a fire door was no longer used as a door and is not required for egress, what methods would you allow to address it?
a) push the storage cabinet against the door and call it a day
b) replace the door with a door equivalent to the wall rating, even though the door can not be opened for a fire door inspection
c) leave the original door and install something else in the door opening too (like a panel) - again the door would not be openable for a fire door inspection
d) remove the door and fill the opening with something similar to the wall construction to maintain the wall rating
e) another method
5.1.2 Removal of Door or Window. Where a door or window opening is no longer in use, the opening shall be filled with construction equivalent to that of the wall.
I posted something on my blog about this (http://idighardware.com/2014/05/ww-hidden-door/), and someone commented that I was wrong...that the door didn't have to be removed, it could be replaced with another door equal to the wall rating, or somehow "treated" to provide the same protection as the wall. I don't think this is commonly done, and once the storage cabinet is against the door, the door may not be able to be opened for the annual fire door inspection to verify the rating or that it is code-compliant.
My question for you is...if a fire door was no longer used as a door and is not required for egress, what methods would you allow to address it?
a) push the storage cabinet against the door and call it a day
b) replace the door with a door equivalent to the wall rating, even though the door can not be opened for a fire door inspection
c) leave the original door and install something else in the door opening too (like a panel) - again the door would not be openable for a fire door inspection
d) remove the door and fill the opening with something similar to the wall construction to maintain the wall rating
e) another method