2009 UPC. We have a plumbing contractor proposing to install a 90 deg turn metering push button valve on a urinal. The valve is a Pasco, part # 21810. This valve does not appear to have a vacuum breaker on it. Has anyone ever seen this valve installed?
I looked into the 2006 IPC to see how it reads as well. It mentions flushometer valves for urinals in chpater 4, but does not refer specifically to section 608 for protection of the water supply, but I'm assuming that a vacuum breaker is required in the IPC based on the wording in 608.1, 608.2.
In UPC section 603.4.1 it specifically couples the requirement for a vacuum breaker with urinals. I have an inquiry into the manufacturer, but they haven't contacted me yet (it's only been a few minutes).
To top it off, the plumber says the same valve is already installed in several business around the city. He mentioned a few, and I will stop in those just for a looksee. Lucky they aren't installed in the ladies restrooms! That could get interesting.
I hope they weren't ones that I finalled!