NM Cable or 'romex' was developed as a less expensive alternative to BX cable back in the early 1920's. Type NM cable has come a long way since then, including the addition of an equipment grounding conductor starting in the very early 1960's. It is synonymous with one and two family dwellings and of course limited in its use for commercial and industrial applications.
When we read through the code for NM cable we see something interesting, not typical in many other code articles. Let's take a look:
334.10 Uses Permitted. Type NM, Type NMC, and Type NMS
cables shall be permitted to be used in the following, except as
prohibited in 334.12:
(1) One- and two-family dwellings and their attached or
detached garages, and their storage buildings.
(2) Multi-family dwellings permitted to be of Types III, IV,
and V construction.
(3) Other structures permitted to be of Types III, IV, and V
construction. Cables shall be concealed within walls,
floors, or ceilings that provide a thermal barrier of material
that has at least a 15-minute finish rating as identified
in listings of fire-rated assemblies.
(4) Cable trays in structures permitted to be Types III, IV, or
V where the cables are identified for the use.
(5) Types I and II construction where installed within raceways
permitted to be installed in Types I and II construction.
When you look at 334.10(5) you immediately think that you can only use NM cable in types I and II construction when installed in raceways, but, that is not the case. Look a little closer at 334.10(2). It may just surprise you.
334.10(2) states "Multi-family dwellings permitted to be of Types III, IV and V construction." What does that mean? The word permitted does not mean that you issued a permit, it means that under the type use, area and height limitations, although the owner chose to build with Type I or II construction, they would have been permitted to build in a lower classification such as Type III, IV or V construction.
I recently looked at a 5 story condo building that was of Type 1 construction but the dwelling units were all wired with NM cable. It was a sprinklered building, of course, but could have easily been built with Type II, IV or V construction. This, of course made the installation of NM cable in the dwelling units perfectly acceptable.

When we read through the code for NM cable we see something interesting, not typical in many other code articles. Let's take a look:
334.10 Uses Permitted. Type NM, Type NMC, and Type NMS
cables shall be permitted to be used in the following, except as
prohibited in 334.12:
(1) One- and two-family dwellings and their attached or
detached garages, and their storage buildings.
(2) Multi-family dwellings permitted to be of Types III, IV,
and V construction.
(3) Other structures permitted to be of Types III, IV, and V
construction. Cables shall be concealed within walls,
floors, or ceilings that provide a thermal barrier of material
that has at least a 15-minute finish rating as identified
in listings of fire-rated assemblies.
(4) Cable trays in structures permitted to be Types III, IV, or
V where the cables are identified for the use.
(5) Types I and II construction where installed within raceways
permitted to be installed in Types I and II construction.
When you look at 334.10(5) you immediately think that you can only use NM cable in types I and II construction when installed in raceways, but, that is not the case. Look a little closer at 334.10(2). It may just surprise you.
334.10(2) states "Multi-family dwellings permitted to be of Types III, IV and V construction." What does that mean? The word permitted does not mean that you issued a permit, it means that under the type use, area and height limitations, although the owner chose to build with Type I or II construction, they would have been permitted to build in a lower classification such as Type III, IV or V construction.
I recently looked at a 5 story condo building that was of Type 1 construction but the dwelling units were all wired with NM cable. It was a sprinklered building, of course, but could have easily been built with Type II, IV or V construction. This, of course made the installation of NM cable in the dwelling units perfectly acceptable.