• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Vapor Retarder in crawlspace

retire09

Silver Member
Joined
Feb 19, 2010
Messages
365
Location
Alaska
Is a vapor retarder required between the floor joists and behind the rim board in a heated crawlspace?

The foundation walls are concrete and a vapor retarder is covering the gound in the crawlspace.

The floor above is not insulated and the crawlspace is not vented.
 
No, as long as you meet the requirements of R408.3, which it appears maybe you do with #2.2, vapor barrier and conditioned air, do you meet the rest of the requirement?
 
What part of the country is the project in.

You may need it to address Radon Gas concerns. Not just energy. Not just subgrade moisture.
 