Thats questionable.Appliance. Utilization equipment, generally other than industrial, that is normally built in standardized sizes or types and is installed or connected as a unit to perform one or more functions such as clothes washing, air conditioning, food mixing, deep frying, and so forth.
Hmm, no compressor in a VAV.440.1 Scope.The provisions of this article apply to electric motor-driven air-conditioning and refrigerating equipment and to the branch circuits and controllers for such equipment. It provides for the special considerations necessary for circuits supplying hermetic refrigerant motor-compressors and for any air-conditioning or refrigerating equipment that is supplied from a branch circuit that supplies a hermetic refrigerant motor-compressor.
What are you questioning? Could you give a brief example of the inconsistent numbers that caught your eye?dcspector said:I have had the opportunity to read several inspecton reports from other juridictions and the section numbers have been inconsistent.
I was probably sober... :lol:chris kennedy said:dcspector said:Also, very odd that an inspector would spell 'inspection' and 'jurisdiction' wrong yet spell 'inconsistent' correctly. :lol:
I agree with you on using Article 424 if the VAV has heat strips and 424.19© specifically allows the use of a unit switch as the required disconnecting means.dcspector said:Chris and Dave,This is regarding disconnecting means for the VAV. Usually the VAV's I deal with have the resistive heat strips/coils. Now with that said the units have the incorporated unit switch per 424.19© is what is and should be accepted. However, the EC's in my area are getting gigged in the surrounding areas for not field providing an additional disconnect. In summarry all I have seen on the other reports were anywhere from rediculous, to 422, 440..