The following 2 code excerpts seem to create a code conflict.
1203.4.1 Ventilation area required. … 4 percent of the floor Area…..
1405.13.2 Window sills. ….. Glazing between the floor and a height of 24 inches shall be fixed or have openings through which a 4-inch diameter sphere cannot pass.
Exception: Openings that are provided with window guards that comply with ASTM F 2006 or F 2090.
1203.4.1 Requires the minimum opening of window for ventilation.
1405.13.2 States if the sill is too close to the floor, you need to restrict the opening. Thereby making your ventilation non-compliant, or does the exception make it all ok? The window is capable of being opened to meet the ventilation minimum, but when it is open, it is in violation of minimum sill height.
I suspect this falls into that old cake and eat it saying.
1203.4.1 Ventilation area required. … 4 percent of the floor Area…..
1405.13.2 Window sills. ….. Glazing between the floor and a height of 24 inches shall be fixed or have openings through which a 4-inch diameter sphere cannot pass.
Exception: Openings that are provided with window guards that comply with ASTM F 2006 or F 2090.
1203.4.1 Requires the minimum opening of window for ventilation.
1405.13.2 States if the sill is too close to the floor, you need to restrict the opening. Thereby making your ventilation non-compliant, or does the exception make it all ok? The window is capable of being opened to meet the ventilation minimum, but when it is open, it is in violation of minimum sill height.
I suspect this falls into that old cake and eat it saying.