Let me try this one more time. Section 1014.3 is the Section that deals with common path of travel. Charging language found there states that in all occupancies other than Groups H-1 / H-2 / & H-3, the common path of egress travel may not exceed 75'. Right?
As with many other code sections, there are exceptions granted. In this particular case, there are four exceptions granted. Remember, just because there are exceptions, they are still under the heading of common path of travel. They are exceptions to the basic requirements of the common path of travel.
In this case one of the exceptions, exception #4 specifically, allows the common path of travel in Group R-2 occupancies to be increased to 125' given certain circumstances. It is still a common path of travel, it may just be lengthened if the building is a sprinkled building. Instead of the common path of travel being 75' as required by the original language, it may now be 125' when the building is sprinkled.
It is still dealing with the common path of travel. The code permits this. Yes I would allow it if the building was a sprinkled building.