• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Vertical Fenestration of Addition and Existing Buildings

admiralArchArch

Registered User
Joined
Nov 30, 2018
Messages
23
Location
middle earth
We are doing a small addition (~3,000SF) to very large school (200,000+ SF). The addition is mostly curtainwall so naturally we are exceeding vertical fenestration limits in per C402.4.1 in 2018 IECC. Trying to run A COMcheck and of course the envelope fails by like -30%.

However, if you look at C502.2.1 you can use the total building fenestration area that includes the existing building. Factoring that in we would be waaaay below 30%, however there is no way to document this via COMcheck. If I plug into COMcheck approximated numbers for existing wall, floor, roof, windows it does not help even using code minimums (probably because the UA values skyrocket).

How do we document compliance without a comcheck as that is what our AHJ is going to be looking for?
 