• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Vertical penetrations in a high-rise

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,071
Location
Somewhere Too Hot & Humid
You see this during a renovation of a dwelling unit inside a high-rise structure that is Type IIA construction with fire sprinklers. Would you allow this?
IMG_6795.JPG IMG_6797.JPG
 
This is not acceptable for a couple of reasons:
  1. The evaluation report from UL indicates it is only suitable for Type VB construction. Since this is a high rise Type IIA construction means they’re using it outside of the approved use.
  2. The penetrations require firestop assemblies tested per ASTM E 814 or UL 1479. This product has NOT been tested per either.
 
This is not acceptable for a couple of reasons:
  1. The evaluation report from UL indicates it is only suitable for Type VB construction. Since this is a high rise Type IIA construction means they’re using it outside of the approved use.
  2. The penetrations require firestop assemblies tested per ASTM E 814 or UL 1479. This product has NOT been tested per either.

I agree. I could not even find an ASTM E84 rating on the can.
 
Give the guy a little credit for trying. It says its good for residential construction, and he used it in a residence. At least it wasnt plain foam.
 
Give the guy a little credit for trying. It says its good for residential construction, and he used it in a residence. At least it wasnt plain foam.
If there are drawings and specifications for the project that require tested firestop assemblies, then no credit is due—they should’ve been familiar with the contract requirements.
 
No

Plus just because it says Fire, does not mean it is directly out of the fire code

A building Code item to me on new and remodel work.
 
If there are drawings and specifications for the project that require tested firestop assemblies, then no credit is due—they should’ve been familiar with the contract requirements.

Yes and when I ask for specs on the drawings I get resistance but this is what happens even when there are specs.
 
Yes and when I ask for specs on the drawings I get resistance but this is what happens even when there are specs.
If I was the architect providing contract administration, I would reject the installation, even if the building accepted it. It is still a breach of contract. The contractor would be required to replace all of the non compliant materials and replace them with compliant materials. If the contractor refuses, the owner has the right to withhold payment on that portion of the work, and if the contractor still refuses to correct the deficiency, the owner can bring in a separate contractor to correct the work and charge the original contractor for the cost.
 
Point, why wouldn't the building have to approve the work first? And then confirm it met code when completed?
 