• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

walk in refer and sprinklers

pwood

Platinum Member
Joined
Nov 3, 2009
Messages
1,067
Location
state of jefferson
Is a sprinkler head required in a walk in cooler less than 50 sq. ft. in a sprinklered building? never ran into this before! thanks! i forgot to mention that this is a self contained factory built unit, not site built.
 
Last edited by a moderator:
In general, if you can walk into it, you sprinkler it. If you reach into it, you don't. Sprinklers are often required on top of walk ins if combustibles are there.
 
Coug Dad said:
In general, if you can walk into it, you sprinkler it. If you reach into it, you don't. Sprinklers are often required on top of walk ins if combustibles are there.
Stop copying me

That has been my mantra for a long time

You sprinkle smaller enclousures than that, and you never know they may turn it off and start storing more stuff in it
 
walk-in type freezers, coolers, vaults and safes require sprinklers

NFPA Formal Interpretation 78-6, these areas require sprinklers because they are part of the premises. NFPA 13 requires that sprinklers be installed throughout the premises in accordance with Section 4-1.1. There are no exceptions provided which allow for sprinkler omission in these areas. Dry pendent sprinkler heads
 
* *

From the `06 IBC, Section 903.3.1.1.1, Exempt locations, #2: Any room or space where

sprinklers are considered undesirable because of the nature of the contents, when

approved by the fire code official.



* *
 
IBC 2012

[F] 903.3.1.1.1 Exempt locations.

Automatic sprinklers shall not be required in the following rooms or areas where such rooms or areas are protected with an approved automatic fire detection system in accordance with Section 907.2 that will respond to visible or invisible particles of combustion. Sprinklers shall not be omitted from any room merely because it is damp, of fire-resistance-rated construction or contains electrical equipment.

1. Any room where the application of water, or flame and water, constitutes a serious life or fire hazard.

2. Any room or space where sprinklers are considered undesirable because of the nature of the contents, when approved by the fire code official.

3. Generator and transformer rooms separated from the remainder of the building by walls and floor/ceiling or roof/ceiling assemblies having a fire-resistance rating of not less than 2 hours.

4. Rooms or areas that are of noncombustible construction with wholly noncombustible contents.

5. Fire service access elevator machine rooms and machinery spaces.

6. Machine rooms and machinery spaces associated with occupant evacuation elevators designed in accordance with Section 3008.

BUT

walk-in type freezers, coolers, vaults and safes require sprinklers

NFPA Formal Interpretation 78-6, is specific regarding walk-in type freezers, coolers, vaults and safes require sprinklers.

There are no exceptions provided which allow for sprinkler omission in these areas.

Dry pendent sprinkler heads
 
Do not forget the dry sprinklers only last for 10 years. So make sure you can get to it to replace it.

NFPA 25, 2011 edition, 2002 ed is the same

5.3.1.1.1.6* Dry sprinklers that have been in service for 10 years shall be replaced or representative samples shall be tested and

then retested at 10-year intervals.
 
Insurance Engineer said:
Do not forget the dry sprinklers only last for 10 years. So make sure you can get to it to replace it.NFPA 25, 2011 edition, 2002 ed is the same

5.3.1.1.1.6* Dry sprinklers that have been in service for 10 years shall be replaced or representative samples shall be tested and

then retested at 10-year intervals.
Because as per the 25-2011 handbook, the failure rate of dry heads tested at 10 years is 50%.
 
fireguy said:
Because as per the 25-2011 handbook, the failure rate of dry heads tested at 10 years is 50%.
Dry pipe systems have some disadvantages which must be evaluated before selecting this equipment. These include:

Increased complexity. Dry pipe systems require additional control equipment and air pressure supply components which increases system complexity. Without proper maintenance this equipment may be less reliable than a comparable wet pipe system.

Higher installation and maintenance costs. The added complexity impacts the overall dry-pipe installation cost. This complexity also increases maintenance expenditure, primarily due to added service labor costs.

Lower design flexibility. There are strict requirements regarding the maximum permitted size (typically 750 gallons) of individual dry-pipe systems. These limitations may impact the ability of an owner to make system additions.

Increased fire response time. Up to 60 seconds may pass from the time a sprinkler opens until water is discharged onto the fire. This will delay fire extinguishing actions, which may produce increased content damage.

Increased corrosion potential. Following operation, dry-pipe sprinkler systems must be completely drained and dried. Otherwise remaining water may cause pipe corrosion and premature failure. This is not a problem with wet pipe systems where water is constantly maintained in piping.

With the exception of unheated building spaces and freezer rooms, dry pipe systems do not offer any significant advantages over wet pipe systems. Their use in buildings is generally not recommended.
 
mark handler said:
With the exception of unheated building spaces and freezer rooms, dry pipe systems do not offer any significant advantages over wet pipe systems. Their use in buildings is generally not recommended.
Dry sprinkler systems do have some problems.

Lack of maintanence is a contributing factor. So far this winter we have had 4 of our dry sprinkler systems freeze and break, one of them has frozen twice. One sprinkler room froze completly, including all the valves, the jockey pump, and the fire pump, and both risers. Each building that has frozen has not had the condensation drained properly. Those buildings with a competent maintanence program have not had a problem.

Installation standards need to be upgraded, concerning both the pipe used and insulation practices.

Schedule 5 and 10 pipe is used because it costs less to install. But 10 to 12 years later, we start replacing rusty pipe. On one repair job I gave the customer 2 choices. We could use schedule 10 or schedule 40. The schedule 40 increased the cost 10%. The customer spent the extra money. Now, we use schedule 40 exclusivly.

We often add auxillary drains to dry systems. We recently did a job and added 30 drains to dry system. The architect could have saved the building owner lots of money over the last 20 years by not having a 48" eave overhang. But the $21,000.00 check I got yesterday was nice.

Replacing rusty pipe is expensive. It may take 7 man-hours to remove and replace a stick of pipe.

Insulation needs to be addressed in NFPA 13. One of our clients had the roof insulated during the build. In 20+ years, We have not had to replace any broken pipes. They have a wet system with an antifreeze loop protecting a small patio and 2 dry heads. No dry pipe system. Another building has plastic tented over the dry piping in the attic, with blown insulation. The building has had no problem with frozen piping in 25 + years. We have had 3" wet pipe systems freeze because of lack of insulation. When a 3 " pipe thaws, everything gets wet!
 
the consensus seems to be yes. they have a sprinkler head above the unit and the plans i approved had one inside. the owner thinks it is absurd to have one in the unit because he feels ice cream won't catch fire! not the first person to think i'm an idiot! :mrgreen:
 
Insurance Engineer said:
Mark, Dry sprinkler = apples Dry Pipe Valve =oranges You are mixing fruits
Each sprinkler operates individually, As the air pressure drops in the piping leading to the sprinklers the pressure differential across the dry pipe valve allows the water to flow.

I am not mixing anything
 