Any one have this sectio used on them before???
1st time in a lot of years some one pulled this on me:
8.6.3.2.3* The requirements of 8.6.3.2.1 shall not apply where walls are angled or irregular, and the maximum horizontal distance between a sprinkler and any point of floor area protected by that sprinkler shall not exceed 0.75 times the allowable distance permitted between sprinklers, provided the maximum perpendicular distance is not exceeded.
1st time in a lot of years some one pulled this on me:
8.6.3.2.3* The requirements of 8.6.3.2.1 shall not apply where walls are angled or irregular, and the maximum horizontal distance between a sprinkler and any point of floor area protected by that sprinkler shall not exceed 0.75 times the allowable distance permitted between sprinklers, provided the maximum perpendicular distance is not exceeded.