• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Was a corridor now not a corridor

Mr. Inspector

SAWHORSE
Joined
Nov 28, 2009
Messages
4,127
Location
Poconos/eastern PA
CORRIDOR. An enclosed exit access component that defines and provides a path of egress travel to an exit.

Alterations being done to a medical office (B). Sprinklered. It had a 70' long exisiting corridor that ended at a waiting room that conneted to a lobby on one end. Other end has a door to a storage room that has an exit door. They want to install a wall across the corridor 30' from the waiting room that will leave 40' of of corridor without an exit. They are planing to have two 3' openings in the corridor wall on either side of the wall that will be built across the existing corridor. that lead into the same office. So a person could go down the 40' section of the corridor, walk through the office and continue back into the 30' corridor to the waiting room and on to an exit. The existing corridor is enclosed and leads to an exit. Now with the 3' openings and the 40' section not leading to an exit can it still be called an corridor or is just an aisle.
 
How many sq ft is the office/ business

Occupant load

Is the building sprinkled

What edition icode
 
Plans only show a part of building, the tenant space which is 3800 sq. ft.. they did not give me a occupancy load but i think it would be about 34. sprinklered. 2009 IBC
 
so they can do non rated corridors

I was going to say because of size and occupant load ,,,, sounds like they need two legal exits, but looks like they are good there

plus does common path of travel come into play???? will that require two legal exits
 
1014.2 Egress through intervening spaces.

Egress through intervening spaces shall comply with this section.

1. Egress from a room or space shall not pass through adjoining or intervening rooms or areas, except where such adjoining rooms or areas and the area served are accessory to one or the other, are not a Group H occupancy and provide a discernible path of egress travel to an exit .

Exception: Means of egress are not prohibited through adjoining or intervening rooms or spaces in a Group H, S or F occupancy when the adjoining or intervening rooms or spaces are the same or a lesser hazard occupancy group.

2. An exit access shall not pass through a room that can be locked to prevent egress.



3. Means of egress from dwelling units or sleeping areas shall not lead through other sleeping areas, toilet rooms or bathrooms.

4. Egress shall not pass through kitchens, storage rooms, closets or spaces used for similar purposes. ​Houston I think you have a problem with this one



Exceptions:

1. Means of egress are not prohibited through a kitchen area serving adjoining rooms constituting part of the same dwelling unit or sleeping unit.

2. Means of egress are not prohibited through stockrooms in Group M occupancies when all of the following are met:

2.1. The stock is of the same hazard classification as that found in the main retail area;

2.2. Not more than 50 percent of the exit access is through the stockroom;

2.3. The stockroom is not subject to locking from the egress side; and

2.4. There is a demarcated, minimum 44-inch-wide (1118 mm) aisle defined by full- or partial-height fixed walls or similar construction that will maintain the required width and lead directly from the retail area to the exit without obstructions.
 
1. 1014.3 Common path of egress travel.

The common path of egress travel shall not exceed the common path of egress travel distances in Table 1014.3.

100 feet max

1015.1 Exits or exit access doorways from spaces.

Two exits or exit access doorways from any space shall be provided where one of the following conditions exists:

1. The occupant load of the space exceeds one of the values in Table 1015.1.

Exceptions:

1. In Group R-2 and R-3 occupancies, one means of egress is permitted within and from individual dwelling units with a maximum occupant load of 20 where the dwelling unit is equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2.

2. Care suites in Group I-2 occupancies complying with Section 407.4.3.

2. The common path of egress travel exceeds one of the limitations of Section 1014.3.

3. Where required by Section 1015.3, 1015.4, 1015.5, or 1015.6.

Over 100 feet???

If two exits are require possible dead in corridor

Plus if two exits are required are they spaced and placed so everyone can get to them

1021.2 Exits from stories.

Two exits, or exit access stairways or ramps providing access to exits, from any story or occupied roof shall be provided where one of the following conditions exists:

1. The occupant load or number of dwelling units exceeds one of the values in Table 1021.2(1) or 1021.2(2).

2. The exit access travel distance exceeds that specified in Table 1021.2(1) or 1021.2(2) as determined in accordance with the provisions of Section 1016.1.

3. Helistop landing areas located on buildings or structures shall be provided with two exits, or exit access stairways or ramps providing access to exits.

over 75 feet ???
 