• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Washing Machine vent pipe

What is the vertical rise? Don't have my books in front of me, bt if memory serves, that is a factor............
 
Skip,

"Washing machine drain is 2" with a 1-1/2" vent that travels 60'. Is the vent sized correctly? "

Yes, see 2006/2009 IRC, Section P3113 Vent Pipe Sizing.

P3113.1 Size of vents. " The minimum required diameter of individual vents, branch vents, circuit vents, vent stacks and stack vents shall be at least one-half the required diameter of the drain served. Vent pipes shall not be less than 1 1/4 inches in diameter. Vents exceeding 40 feet in developed length shall be increased by on nominal pipe size for the entire developed length of the vent pipe."

2" drain = 1" vent; except that the least vent size allowed is 1 1/4". Over 40 feet developed length = one "nominal pipe size" increase. So actually 1 1/4" would meet the code requirements.

Interesting note about not allowing less than 1 1/4" vent pipe. Your not going to believe it, but, 1" vents whistle. :)

Hope this helps,

Uncle Bob
 