Certainly not when the water closet connects to a stack rather than directly to the building drain.The water closet is a "branch of the building drain"
Fair enough. I was looking at the water closet labeled "fixture drain", did not notice the one that was on the same branch as the LAV and the VTR.Certainly not when the water closet connects to a stack rather than directly to the building drain.
Cheers, Wayne
That is crazy... why would someone do that?I have a submittal showing a 2" from the w/c connection to the point it picks up another fixture.
Because the "2" button is right next to the "3" button and they have fat fingers?That is crazy... why would someone do that?
Code reference? All I see is for a building drain.But
according to the International Plumbing Code (IPC), and the International Residential Code (IRC) , the minimum size of a water closet fixture drain is 3 inches
T709.2 is for fixtures not listed in t709.1, and a 1.6 w/c is listed so we use t709.1. T709.1 shows 4 DFU's for 1.6 w/c, with two notes that say you can't reduce the DFU load for a building drain without jumping through a hoop and that the trap size is dependent on the fixture outlet, but that doesn't make a lot of sense to me since the trap is integral and is upstream of the fixture outlet (when are they not for a w/c?). Even if we used t709.2 and the DFU's from t709.1 the fixture drain would be 2 1/2".IPC 740.2 says "The size of the drainage piping shall not be reduced in the direction of the flow." Since you can't have a 4" fixture drain going into a 3" building drain, 3" is OK.
Also, Table 709.2 allows 5 FU on a 3" fixture drain, and a WC is 3 or 4 FU, except for a public toilet greater than 1.6 gal per flush, and Table 710.1(2) allows 20 FU on a 3" fixture branch.
I went down the branch path, but it just doesn't seem to hold water (sorry). I agree the intent may be there, but for this it would seem to be too easy to have just stated that a w/c fixture drain is 3" min. The commentary for the definition of branch even says a fixture drain doesn't become a branch until it merges with another fixture drain. To me it seems it either got lost somewhere along the way or assumed. FWIW the 2009 UPC (most recent version I have) explicitly requires a 3" "trap arm" for a water closet. However it also says a 3" trap is required. Is there anything different in the more recent UPC's?As stated on this forum before ICC does not mean Intelligent Clear or Concise but I believe the intent of footnote (a) of Table 710.1(1) is a minimum 3" for a water closet
TABLE 710.1(1)
BUILDING DRAINS AND SEWERS
MAXIMUM NUMBER OF DRAINAGE FIXTURE UNITS CONNECTED TO ANY PORTION OF THE BUILDING DRAIN OR THE BUILDING SEWER, INCLUDING BRANCHES OF THE BUILDING DRAIN a
a. The minimum size of any building drain serving a water closet shall be 3 inches.
BRANCH. Any part of the piping system except a riser, main or stack.
See how easy it can be?2018 UPC
View attachment 15026