• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Water Heater electrical code violation by design

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,051
Location
Somewhere Too Hot & Humid
I just caught this one in plan review and though I would add this as some trivia. Here is the situation.

Level 2 remodel of condo which includes a new water heater
The panel schedule showed the following:

A double pole 60A breaker with #6awg cu wire to a 4500w electric storage water heater.

What is the NEC violation? Cite the code please.
 
334.80 says that NM cable shall be sized according to the 60 degree C column (310.16), which allows 55 amps on a 6AWG wire.

422.11(E)(3) says the branch circuit for a storage type water heater shall not exceed 150% of the device's rated current if the overcurrent protection is not marked.

4500 watts / 240 volts = 18.75 amps. 18.75 amps x 150% = 28.125 amps.

They need a 30 amp circuit maximum.

2020 NEC
 
Last edited:
334.80 says that NM cable shall be sized according to the 60 degree C column (310.16), which allows 55 amps on a 6AWG wire.

422.11(E)(3) says the branch circuit for a storage type water heater shall not exceed 150% of the device's rated current if the overcurrent protection is not marked.

4500 watts / 240 volts = 18.75 amps. 18.75 amps x 150% = 28.125 amps.

They need a 30 amp circuit maximum.

2020 NEC
B I N G O

Since this is a condo, high-rise, however, there is no NM cable and more than likely this is in EMT with THHN.
 