• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Water Heater Expansion Control

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,021
Location
Somewhere Too Hot & Humid
In place of an expansion tank, we now approve this device which then adds a second discharge tube to the drain pan or wherever your situation allows it to terminate.
1C91047F-098B-43BF-A00A-9C53FAA95944.jpeg
 
In place of an expansion tank, we now approve this device which then adds a second discharge tube to the drain pan or wherever your situation allows it to terminate.

I am not convinced that discharging to a drain pan is a suitable solution. The devices will operate at a setting from 80 psi on up. At a setting of 80 psi it would open but as soon as it hits 79 psi it closes. Upon opening the psi would drop below 80 psi immediately if it were reacting to thermal expansion. There would be a short burst of water that may or may not be contained in a smitty pan. If the valve opened due to a service pressure above 80 psi the flow would continue until the service pressure went below 80 psi. That would overwhelm a drain pan. The next highest setting is 120 psi which is putting stress on the entire plumbing system.
 