• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Water Heater Seismic Strapping question

righter101

Gold Member
Joined
Dec 5, 2009
Messages
604
IRC & UPC require seismic strapping of water tanks at the upper 1/3 and lower 1/3 points. Code is pretty clear.

Anyone allow by modificaiton use of a single strap on the stubby 30 gallon ones??

Just curious.

Hope everyone is well.
 
righter101 said:
IRC & UPC require seismic strapping of water tanks at the upper 1/3 and lower 1/3 points. Code is pretty clear.Anyone allow by modificaiton use of a single strap on the stubby 30 gallon ones??

Just curious.

Hope everyone is well.
I don't recall anyone ever having asked me to approve such an arrangement. Restraining 380 pounds deserves two straps. Just ask Fatboy.
 