watts per foot rule of thumb for Lab Generator load
mshields
Silver Member
Plymouth, MA
If you were doing a core and shell for a building that would be filled with labs but for whom the tenants had not yet been established, what watts per square foot of lab space would you use as a safe number sizing your Optional Standby Generator or generator(s) which are to be provided under the base building?
Mike,
Some additional basic information would be needed for a proposed calculation.
How many "gennies" & the amperage of each to start with.
36Wft²
Based on 2000A 208y/120V for 20,000ft² building. Safe bet, maybe for optical lab, State Health Dept lab, ect. Landlord leases to printing operation instead you may want to use the same watt per ft² at 480y/277. ;)
"That's a big horse their putting before the cart."
I agree, but with some more information, we might givesome direction for him to go in, ...albeit "an inaccurate
load calc." based on the tenant space square footage
only [ i.e. - lighting loads, ...general use receptacles,
...motor loads, etc.......RE: Article 220, ...430, & 700,
in the NEC ].
Chris,
Thanks for the input !.......On behalf of the forum viewers and others,
may I please ask you to provide the pathways to which you arrived
at the " 36W per sq. ft. " amount ?.....Thanks !
The various Articles and calculations help me greatly ! :agree
NS, no arts to quote but based on experience a 20,000ft² lab for uses as I described above we usually will see a 2000A 208y/120. Soooo...
2000A×360=720,000va or loosely translated for this exercise watts (360 based on 208V×1.73 for 3Ø)
720,000w÷20,000ft²=36watts per ft²
Thank You Chris for your input ! :D
Can we approach the topic with actual Articles from the NEC to
apply some sort of a calculated "guess-timate" ?.......Granted,
Mike will need to supply some more basic info.
No disrespect intended Chris, but rather than your experience,
...can the question be addressed by using the NEC and its various
Articles ?......REASON: We code officials get asked some pretty
outlandish questions from developers, ...contractors, ...home-
owners, ...colleagues & everyone else in-between.......By having
at least some ideas of how to address the problem; from a
printed Standard, and in which direction to assist the customer,
...we haven't (1) left them with negative impression of our AHJ,
...(2) we have demonstrated a sincere effort to assist in their
problem, ...(3) we have promoted a desire to have a relationship
with that customer, however small or insignificant it may seem
at the moment, which "MAY" result in them having a business
located in our / your AHJ, ...(4) we may actually learn something
from the exercise, ...(5) the customer may leave with a little
clearer understanding of the problem, ...what other questions
to ask, and who to go to find their answers, and (6) others who
visit this Forum and view this topic may also learn something,
...and maybe, just maybe, ...they too will want to join and
become a Sawhorse.
FWIW, ...I regularly get asked to "show me that requirement
or section in the codes !".........I already have an uphill battle in
interpreting & administering the various codes, so the more
[ accurate ] information I can provide, ...the easier it is for
me to have a legitimate position on the matter, and over time,
...to [ hopefully ] build a positive image for myself and my
AHJ !
No way to even venture a guess at a 220 calc with the info Mike has given. Sorry NS, I understand where you coming from.
What is the generator for? exiting? lighting? continuing lab operations? refrigeration? Hoods? filtering ventilation?
That was going to be my question too, Mark.. I just didn't scroll all the way down. The emergency lighting should be picked up by the main generator.