Question
What are the sound level requirements for audible appliances in sleeping areas according to NFPA 72?Answer
According to NFPA 72, audible appliances installed to provide signals in sleeping areas must meet specific sound level requirements to ensure they can effectively wake occupants. Here are the key requirements:Requirements
18.4.6.1When installing audible appliances in sleeping areas, they must produce a sound level that is either:- At least 15 dB above the average ambient sound level, or
- 5 dB above the maximum sound level with a duration of at least 60 seconds, or
- At least 75 dBA, whichever is greater.
18.4.6.2If there is any barrier, such as a door, curtain, or retractable partition, between the notification appliance and the pillow, the sound pressure level must be measured with the barrier in place. This ensures the sound can still effectively reach the sleeping person despite any obstructions.
Additional Considerations
Even though the requirement in 18.4.6.2 specifically applies to sleeping areas, it is good practice to use the worst-case conditions for all ambient and alarm sound level measurements. This means testing with barriers like doors both open and closed to ensure the required sound levels are met in both situations.The sound reduction through a bedroom door can vary based on its construction and fit. In some cases, achieving the required 75 dBA sound level inside the bedroom with an appliance located outside the room may not be possible. In other cases, it might be achievable, but the sound level near the audible appliance could exceed the maximum permitted 110 dBA as per 18.4.1.2.
To ensure the effectiveness of audible alarms in sleeping areas, NFPA 72 requires that these alarms be significantly louder than the surrounding noise, taking into account any barriers that might affect sound transmission. This helps ensure that alarms can wake occupants even in less-than-ideal conditions.