• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

What does that mean? IMC 403.2.1(3)

rktect 1

SILVER MEMBER
Joined
Oct 20, 2009
Messages
1,158
Location
Illinois
Seriously, what does this mean? It states recirculation is prohibited. Next sentence it is not prohibited. The third sentence, it is prohibited again.
 
Is this the language you are referring to? "Where mechanical exhaust is required by Note b in Table 403.3.1.1, recirculation of air from such spaces shall be prohibited. Recirculation of air that is contained completely within such spaces shall not be prohibited. Where recirculation of air is prohibited, all air supplied to such spaces shall be exhausted, including any air in excess of that required by Table 403.3.1.1."

Note b. "Mechanical exhaust required and the recirculation of air from such spaces is prohibited. Recirculation of air that is contained completely within such spaces shall not be prohibited (see Section 403.2.1, Item 3)."

Ok, doing my best to convert this over to plain language using a smoking lounge as an example. A smoking lounge requires mechanical exhaust per Note b in Table 403.3.1.1. It is not permissible, per the first sentence of 403.2.1(3) to recirculate this air to other parts of the building. The second sentence does allow for the recirculation of the air if that air (presumably contaminated) is completely contained to that space (i.e. a dedicated HVAC unit).

2015 IMC Commentary is pictured below...
 

Attachments

  • IMG_0357[1].JPG
    IMG_0357[1].JPG
    1.8 MB · Views: 11
  • IMG_0358[1].JPG
    IMG_0358[1].JPG
    1.9 MB · Views: 11
I was looking at a dog grooming business. Same exact notes and code section. So as long as the dog grooming business, which is like 1200 sq. ft. in area, has its own HVAC system, it can recirc that air all day long?
 
Still needs the minimum ventilation air, so a portion will need to be exhausted and fresh air brought in.
 
I have always taken it that it can be recirculated if it is the same air you are sucking up and then just moving it to another portion of the same environment.
 
Back
Top