Sifu
- Joined
- Sep 3, 2011
- Messages
- 3,576
NEC 2014
230.6 Conductors Considered Outside the Building.
Conductors shall be considered outside of a building or
other structure under any of the following conditions:
(1) Where installed under not less than 50 mm (2 in.) of
concrete beneath a building or other structure
(2) Where installed within a building or other structure in a
raceway that is encased in concrete or brick not less
than 50 mm (2 in.) thick
The condition we are looking at is a cluster of service cables in PVC conduit, running in an 18" crawlspace, on the dirt. The floor above is a metal deck and concrete slab. The question is whether this meets condition #1 since it is under 2" of concrete and would be permitted as beneath a building, or do they need to be encased as in #2. IF running these conduit, under a concrete floor, under a building (in the crawl) meets #1, then t300.5 would allow 0" of burial and would appear to be allowed. This is an existing office building undergoing a remodel. The crawlspace is only accessible by hatch and crawling. Some here believe the conduit needs to be encased, some believe it is OK as is. Since the code appears to make a distinction between under and encased I am not sure. Opinions?