What exactly is a Level 2 alteration per the IEBC?
Discussion.
Scope. Level 2 alterations include the reconfiguration of space, the addition or elimination of any door or window, the reconfiguration or extension of any system, or the installation of any additional equipment.
Therefore, I ask you:
1) Does the installation of an AC system in a building that does not have one, constitute Level 2?
2) Is the addition of new receptacles (extending the electrical system) for a remodeled room (not moving walls or doors) justification for Level 2?
3) Would plans to completely gut down to the studs, the 1st floor of a 3 story apartment building, then replace all existing wiring, and mechanical systems with new, constitute a Level 2 alteration?
1. Absolutely
2. No, unless they are running new circuits and then maybe.(Most likely running new circuits for a pretty specific reason)
3. Absolutely
Depends, does the 1st floor exceed 50% of the aggregate area of the building? If not it is just a Level 2
405.1 Scope.
Level 3 alterations apply where the work area exceeds 50 percent of the aggregate area of the building.