What is 'Nominal' in Voltage
Since the majority of the NEC revolves around AC voltage, I want to stick with that. The NEC references the word nominal when describing voltage, but does not define what nominal is. How do I know that we are not talking about peak-to-peak voltage? We all assume that nominal voltage would be the true RMS voltage, but where does the NEC actually define the word or meaning of nominal?
NEC 220.5aNEC® section 220.5(A), unless other voltages are specified, for purposes of calculating branch-circuit and feeder loads, nominal system voltages of 120, 120/240, 208Y/120, 240, 347, 480Y/277, 480, 600Y/347, and 600 volts shall be used.
Sure it does, see Article 100. From the 2017 NEC (last version available from the publisher in PDF, as far as I known):
2017 NEC Article 100 said:
Voltage, Nominal. A nominal value assigned to a circuit or system for the purpose of conveniently designating its voltage class (e.g., 120/240 volts, 480Y/277 volts, 600 volts). (CMP-1)
Informational Note No. 1: The actual voltage at which a circuit operates can vary from the nominal within a range that permits satisfactory operation of equipment.
Informational Note No. 2: See ANSI C84.1-2011, Voltage Ratings for Electric Power Systems and Equipment (60 Hz).
Informational Note No. 3: Certain battery units may be considered to be rated at nominal 48 volts dc, but may have a charging float voltage up to 58 volts. In dc applications, 60 volts is used to cover the entire range of float voltages.
Presumably ANSI C84.1-2011 will tell us that nominal voltage ratings are RMS based for AC voltages.
Cheers, Wayne
If I understand the question...As I remember "nominal voltage" would be "120v" is 120v +/- 10 volts, or +/- 15 volts without a lot of unnecessary explanation, and understood to be waveform AC.
220 might be 215 to 225 volts.
Nominal voltage does not take into consideration a plus or minus 10%. Nominal is used for load design calculations. NEMA design criteria for motor design can use a plus or minus value for run performance.