• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

What is wrong with this?

(1) SABCs should be 1.5 kVA each.

(2) K111.6 requires that the smokes be on a lighting circuit. But if the dwelling unit meets the scope of 101.2 Exception, then the IBC wouldn't apply, and we'd have to check the IRC for an equivalent requirement. I don't believe the NEC has such a requirement.

Cheers Wayne
 
(1) SABCs should be 1.5 kVA each.

(2) K111.6 requires that the smokes be on a lighting circuit. But if the dwelling unit meets the scope of 101.2 Exception, then the IBC wouldn't apply, and we'd have to check the IRC for an equivalent requirement. I don't believe the NEC has such a requirement.

Cheers Wayne
Excellent. First reply gets it. Nice!
 
Seems odd that the panel would be surface mounted in a dwelling unit. Also note 3 calls for GFCI breakers, where is the note calling for AFCI breakers?
 
Seems odd that the panel would be surface mounted in a dwelling unit. Also note 3 calls for GFCI breakers, where is the note calling for AFCI breakers?
Those are excellent observations. This is typical of cut and paste by design professionals of record. I can guarantee you that the panel will be flush mounted and the panel schedule won't look anything like what is on the plans as this is an existing unit. This is in a condo so it is not 120/240, it is 208. We can reject this stuff all day long or just approve it and trust that the inspectors will catch everything in the field. This is an example of the laziness of the design professionals and common on 99% of projects.
 
This is typical of cut and paste by design professionals of record. This is an example of the laziness of the design professionals and common on 99% of projects.
Cut and paste it's going to be the death of architecture and structural engineering! These days everything we see is basically stolen from something else. Make you really wonder what they are getting paid for or how much engineering they actually are doing for most projects.
 
Cut and paste it's going to be the death of architecture and structural engineering! These days everything we see is basically stolen from something else. Make you really wonder what they are getting paid for or how much engineering they actually are doing for most projects.
While I generally say cad being the cause, I agree. Cut and paste coupled with the growth in sheet counts. Saw high schools done in 50 sheets and worked on one near 1000. Who can review and coordinate 1000 sheets? Glad I retired (before learning Revit!) Maybe when experienced old timers began in cad, things will get righted a little.
 
Should the fridge and wine cooler count per 220.82 B as part of the calculation? Seems like an arguement could be made either way
 
Seems like an arguement could be made either way
The wine cooler is most likely fixed in place while the refer is cord and plug. That is truly "either way"

I wouldn't fault them for overdoing things such a 3 kVa for SABC and a refer. I suppose 0.33 amps deserves to disappear given that fat thumb on the scale but I would still fault them for rounding down on the total load.....admittadly, I have bad habits.
 