For a new dental office, or an alteration to an existing one with medical support gas (instrument air) and a vacuum system, is a 3rd party med-gas inspection and certification required? I would require it for piped medical gas such as oxygen and nitrous oxide, but I am not sure for the instrument air. This would be a level 3 system per NFPA 99, and from what I can tell the vacuum system might trigger it.
5.3.1.3 Wherever the term vacuum occurs, the provisions
shall apply to all piped systems for vacuum.
Per NFPA 99 it looks like the gas is only considered medical gas if it is oxygen or nitrous oxide.
5.3.1.2 Wherever the term medical gas occurs in Level 3, the
term shall apply to all piped systems of nitrous oxide and oxygen
only.
However, this statement is still making me scratch my head:
3.3.80 Instrument air.....Instrument air is a medical
support gas that falls under the general requirements for
medical gases. (PIP)
5.3.1.3 Wherever the term vacuum occurs, the provisions
shall apply to all piped systems for vacuum.
Per NFPA 99 it looks like the gas is only considered medical gas if it is oxygen or nitrous oxide.
5.3.1.2 Wherever the term medical gas occurs in Level 3, the
term shall apply to all piped systems of nitrous oxide and oxygen
only.
However, this statement is still making me scratch my head:
3.3.80 Instrument air.....Instrument air is a medical
support gas that falls under the general requirements for
medical gases. (PIP)