A single change in elevation is not a flight nor a stairway as defined by the model IBC, thus single changes in elevation do not require handrails, the IBC even has an exception that says so, not sure why, but it does.
A single riser does not need hand rails because a single riser is not allowed in most cases.
1003.5 Elevation change. Where changes in elevation of less
than 12 inches (305 mm) exist in the means of egress, sloped
surfaces shall be used. Where the slope is greater than one
unit vertical in 20 units horizontal (5-percent slope), ramps
complying with Section 1012 shall be used. Where the difference
in elevation is 6 inches (152 mm) or less, the ramp shall
be equipped with either handrails or floor finish materials
that contrast with adjacent floor finish materials.
Exceptions:
1. A single step with a maximum riser height of 7
inches (178 mm) is permitted for buildings with
occupancies in Groups F, H, R-2, R-3, S and U at
exterior doors not required to be accessible by
Chapter 11.
2. A stair with a single riser or with two risers and a
tread is permitted at locations not required to be
accessible by Chapter 11 where the risers and treads
comply with Section 1011.5, the minimum depth of
the tread is 13 inches (330 mm) and not less than
one handrail complying with Section 1014 is provided
within 30 inches (762 mm) of the centerline of
the normal path of egress travel on the stair.
3. A step is permitted in aisles serving seating that has
a difference in elevation less than 12 inches (305
mm) at locations not required to be accessible by
Chapter 11, provided that the risers and treads comply
with Section 1029.13 and the aisle is provided
with a handrail complying with Section 1029.15.
Throughout a story in a Group I-2 occupancy, any change
in elevation in portions of the means of egress that serve nonambulatory
persons shall be by means of a ramp or sloped
walkway.