Good morning everyone, I've got a question about egress from a roof deck. It's a fairly small building, roughly 25,000 SF per floor. There are two floors above grade (underground parking below). This is in CA under the 2019 CBC. Schematic plan attached.
I've got two interior exit stairs to empty the building. There is a 2FL deck (over enclosed space below) that is large enough to need two exits from it.
First a philosophical question - where does the "exit access", "exit", and "exit discharge" exist for this deck? I'm sending half the folks to the interior stairway so that "exit" is obviously the stairway door. Where is the second "exit"? Is it the top of the open exterior stairway? The bottom?
And a practical question - For exterior stairway #3 - does it trigger the need for exterior wall protection where it runs parallel with the building (red on attached)?
I'm assuming Stair #3 is an exterior exit stair and must comply with 1027. 1027.6 requires a separation from the interior, but does exception #2 apply?
Exception #2 - separation from the building not required where exit stairway is served by a balcony (the deck?) that connects two approved exits (1, the stairway in question and 2, the interior exit Stair #2)?
Any insight would be appreciated. This is all about putting windows in that red area (non-rated windows).
Thank you,
Neal
I've got two interior exit stairs to empty the building. There is a 2FL deck (over enclosed space below) that is large enough to need two exits from it.
First a philosophical question - where does the "exit access", "exit", and "exit discharge" exist for this deck? I'm sending half the folks to the interior stairway so that "exit" is obviously the stairway door. Where is the second "exit"? Is it the top of the open exterior stairway? The bottom?
And a practical question - For exterior stairway #3 - does it trigger the need for exterior wall protection where it runs parallel with the building (red on attached)?
I'm assuming Stair #3 is an exterior exit stair and must comply with 1027. 1027.6 requires a separation from the interior, but does exception #2 apply?
Exception #2 - separation from the building not required where exit stairway is served by a balcony (the deck?) that connects two approved exits (1, the stairway in question and 2, the interior exit Stair #2)?
Any insight would be appreciated. This is all about putting windows in that red area (non-rated windows).
Thank you,
Neal