Question: at what height does a steeply sloped "stadium"-style floor in a single-story building get considered as an "interior balcony" or "gallery" per CBC 1028.5, requiring a means of egress that leads DIRECTLY to an exit instead of just going down to the main floor?
Background: I have another church project where the sanctuary was originally built with a flat floor in 1991. In 1999 they secured permits to created stadium-style seating. Unfortunately, that project did not have an architect who successfully resolved lines-on sight, and now they want to further modify the floor to be even steeper.
The finished effect will be similar in layout to a movie theater, where occupants enter via "tunnels" at the main floor, at the middle cross-aisle. In order to get to the sloped seating at the rear of the sanctuary, they go up aisles with stairs, so the row just behind the cross aisle is 5' above the main floor. The floor keeps sloping up to the rear of the building. The area underneath the sloped seating is dead space / unoccupied.
Does not sound like you have a 1028.5 and terms not defined
How about travel distance problems???
1028.5 Interior balcony and gallery means of egress. For
balconies, galleries or press boxes having a seating capacity of
50 or more located in Group A occupancies, at least two means
of egress shall be provided, with one from each side of every
balcony, gallery or press box and at least one leading directly to
an exit.
1 a platform that projects from the wall of a building and is enclosed by a parapet or railing
2 an interior projecting gallery in a public building (as a theater)
Balcony." Merriam-Webster.com. Merriam-Webster, n.d. Web. 10 July 2014. .
seem like you have
1028.9 Assembly aisles are required. Every occupied portion
of any occupancy in Group A or assembly occupancies accessory
to Group E that contains seats, tables, displays, similar fixtures
or equipment shall be provided with aisles leading to exits
or exit access doorways in accordance with this section. Aisle
accessways for tables and seating shall comply with Section
1017.4.
1028.11 Assembly aisle walking surfaces. Aisles with a slope
not exceeding one unit vertical in eight units horizontal
(12.5-percent slope) shall consist of a ramp having a slip-resistant
walking surface. Aisles with a slope exceeding one unit
vertical in eight units horizontal (12.5-percent slope) shall consist
of a series of risers and treads that extends across the full
width of aisles and complies with Sections 1028.11.1 through
1028.11.3.
Thanks, TheCommish. so, it would appear that since the sloping stadium floor does not "project" from the building walls (because it is fully enclosed below), it is neither a balcony nor a gallery.