• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

when is your service maxed?

syarn

Silver Member
Joined
Jan 20, 2010
Messages
251
Location
Philadelphia, Pennsylvania, United States
if an engineer says

"...The electrical panel is 400amp/240v/1 ph

We currently have 335 amps connected to the panel before the addition of the dishwasher

The dishwasher will overload the panel..."

the dishwasher looks to have 50 rated amps, 60 amp minimum supply circuit conductor ampacity & 60 amp maximum overcurrent protective device per the spec sheet.

when I add 50 amps to 335 amps I get 385 amps how does that over load the panel?
 
I would ask how you determined that you have 335 amps connected to the panel. Did you add the breakers or do a calculation?
 